120/240, high leg open delta and closed delta

Status
Not open for further replies.

Volt-Amps

Member
Location
Indianapolis
Regards,
I have 2 questions:
1. Is there 120/240, high leg, open delta and 120/240, high leg closed delta?
2. If yes, what is the difference?
3. If yes, and I am inspecting an existing panelboard, how can I determine the service voltage if label is missing and conductors are not color coded.
Thank You
 
Regards,
I have 2 questions:
1. Is there 120/240, high leg, open delta and 120/240, high leg closed delta?
Yes

2. If yes, what is the difference?
The open Delta only has 58% capacity of the closed Delta.

3. If yes, and I am inspecting an existing panelboard, how can I determine the service voltage if label is missing and conductors are not color coded.
Sorry, you will not like my reply but, why are you inspecting something you do not have a good understanding of?

Roger
 