eds

Senior Member
When you have a single phase service drop as part of a 3 phase 120/240 high leg service arrangement do you calculate that single phase part of the service at 240v or at 240*1.732
 

eds

Senior Member
Yes, 600 amp ct service with a 200 amp 3 phase riser and a 400 amp single phase riser
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Sounds like a single service with two service disconnects to me. That is fairly common high leg services. Reduces the risk of 120 volt loads being connected to the high leg.
 

eds

Senior Member
So one more questions, I need to add another 200 amp 3 phase disconnect to this same drop. I have 3 phase rooftop and then the rest will be single phase load. Do I do a separate calculations for the three phase and single phase loads. Single phase loads our for a cafe equipment
 
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
So one more questions, I need to add another 200 amp 3 phase disconnect to this same drop. I have 3 phase rooftop and then the rest will be single phase load. Do I do a separate calculations for the three phase and single phase loads. Single phase loads our for a cafe equipment
Let the POCO know how your load is changing. Is the existing 3 phase service large enough to handle this load or are you adding another 3 Ph service disconnect?
 
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
Forget the 3 phase load for now. Calculate the single phase service. What is it? xxx amp.

Forget the 1 phase load. It doesn't matter. Calculate the three phase load. What is it?
yyy amp.

Tell the POCO each of those loads. Separately. You have xxx amp single phase. You have yyy amp three phase.
 

eds

Senior Member
Let the POCO know how your load is changing. Is the existing 3 phase service large enough to handle this load or are you adding another 3 Ph service disconnect?
Adding a additional 3 phase 200 amp disco to handle the new 3 phase load and the new single phase load
 