Was wondering if you guys can help me determine the demand load amps?
I have a residential multi-family building, 60 residential units at 120/240 volts, single phase totaling 180,000VA on the A,C phases since the B phase is the highleg. All the residential units are fed from a 120/240 volt, single phase meter bank.
For the common area: I have 10,000VA of lights and receptacles on A,C phase. I have a 30HP elevator motor totalling 33,000VA spread out on all three phases. And ten 5KW 240 Volt,single phase wall heaters spread out on all three phases. AB,BC,AC and so on..
What would be the total demand amps if my voltage is 120/240volt 3 phase, 4 wire?
Thanks