120/240 VS 120/208 label/listing.

Status
Not open for further replies.

220/221

Senior Member
Location
AZ
New three phase service for sale. It is labeled 800 amps, 120/240 by the MFG.

I assume that the components are the same for 120/208 as for 120/240 but since the MFG label says 120/240, can it be used for 120/208 installation (without taking off the tag:cool:)?

I notice that most stock gear is labeled 250V but occaisionally I see a specific 120/240 or 120/208 tag.

Technical foul?
 

220/221

Senior Member
Location
AZ
My bad...service equipment for sale.

A supplier of mine wanted my opinion (for some odd reason) and I told him I'd ask someone who knows.




Me? I'd just make a new label at a trophy shop.

208/240.........whatever it takes
 
the panel might be specifically for 120/240v 3ph with the high leg, IIRC the bus is constructed so you can't put a 1p breaker on the high leg phase. They cost extra... some areas will allow you to use a 'standard' panel and tag it with 'high leg' or some such wording, but around Chicago some towns are really specific about what panel will be allowed on 240v services.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
the panel might be specifically for 120/240v 3ph with the high leg, IIRC the bus is constructed so you can't put a 1p breaker on the high leg phase.

I do not know of any panel construction that will prevent you from putting a 1-pole breaker into a 3-pole space. however, I have seen panels built with one part of the bus configured and labeled for 3-pole breakers, and another part built and labeled for 1 & 2-pole breakers (the high leg is missing in this part)

FWIW, technically a three phase high leg system should be referred to as 240/120 (I like to include 3P 4W).
 