32Lateralus
Member
- Location
- West Coast
- Occupation
- Electrical
So I am unfamiliar with this system as all my design time so far has been on 208V and 480V systems. I have been asked to take a look at a building that has a 120/240V 3ph delta system, with a '3-pot bank' which seems to mean 3 individual pole mounted xfmrs making a closed delta with a high leg. Is this all correct to start?
My understanding is (assuming B as high leg):
A-N: 120V
B-N: 208V
C-N: 120V
All L-L is 240V
Now where I am uncertain is can 3 phase loads such as motor loads be connected to this system as long as they are rated 230V 3ph?
When calculating 3ph load would the voltage be 240V*sqrt(3) ~ 415V
So a 10A, 230V 3ph motor load.... 10A * 415V ~ 4150VA.... and is this distributed equal on the phases so 1383VA per phase?
Let me know if there is anything I am missing