120/240V panel… All loads are 120V…

Merry Christmas

Cindysparky

Member
Location
Milwaukee
Occupation
Electrician
Simple problem that I’m not sure of the answer: 120/240V panel. All loads are 120V

I’m assuming you just take A phase minus B phase to calculate the Amps on the neutral. Am I correct?

Thanks :)
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Welcome to the forum.

It's literally based on the maximum imbalanced load you can place on either line.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
For single phase 120/240 it's as simple as this illustration.

1729436491451.png
 

Cindysparky

Member
Location
Milwaukee
Occupation
Electrician
I’ve seen that a million times for one a multi-wire branch circuit, but I didn’t want to oversimplify it for a panel feeding many circuits. Thanks everyone. I needed this help.
 

eric stromberg

Senior Member
Location
Texas
Imagine a power failure on one line. If line 1 fails, what is the load on line 2? If line 2 fails, what is the load on line 1? Whatever the larger load is, is the minimum size for your neutral.
 