A friend of mine called me for some help to wire a safety switch (Pull out type) that powers a 120v pool pump (its an older pump).
Most of the safety switches say "240 volt" on the shelf, but there was a single one that said "120/240". He bought that one but called me first. I never really seen a safety switch labeled as 120/240 so I asked him to open it to see if there was a neutral bus isolated from the case and ground bus but it was sealed so couldn't open it.
I started to look into the code to see if this was mentioned but couldn't find anything. With that said, I don't see why it wouldn't work to just hook up the incoming neutral to the "Load" and the neutral to the pump on the "Line" terminal.
There's a single copper plate that connects the loads and the pull out is designed to disconnect everything simultaneously, even if you were to pull at an angle. Essentially it can only be inserted directly straight into the safety switch.
Just curious if this is in the code anywhere so I know for future reference and to satisfy curiosity.
PS: As I was typing this I came across NEC 430.105. Pretty sure its legal...
Most of the safety switches say "240 volt" on the shelf, but there was a single one that said "120/240". He bought that one but called me first. I never really seen a safety switch labeled as 120/240 so I asked him to open it to see if there was a neutral bus isolated from the case and ground bus but it was sealed so couldn't open it.
I started to look into the code to see if this was mentioned but couldn't find anything. With that said, I don't see why it wouldn't work to just hook up the incoming neutral to the "Load" and the neutral to the pump on the "Line" terminal.
There's a single copper plate that connects the loads and the pull out is designed to disconnect everything simultaneously, even if you were to pull at an angle. Essentially it can only be inserted directly straight into the safety switch.
Just curious if this is in the code anywhere so I know for future reference and to satisfy curiosity.
PS: As I was typing this I came across NEC 430.105. Pretty sure its legal...