Npstewart

Senior Member
A friend of mine called me for some help to wire a safety switch (Pull out type) that powers a 120v pool pump (its an older pump).

Most of the safety switches say "240 volt" on the shelf, but there was a single one that said "120/240". He bought that one but called me first. I never really seen a safety switch labeled as 120/240 so I asked him to open it to see if there was a neutral bus isolated from the case and ground bus but it was sealed so couldn't open it.

I started to look into the code to see if this was mentioned but couldn't find anything. With that said, I don't see why it wouldn't work to just hook up the incoming neutral to the "Load" and the neutral to the pump on the "Line" terminal.

There's a single copper plate that connects the loads and the pull out is designed to disconnect everything simultaneously, even if you were to pull at an angle. Essentially it can only be inserted directly straight into the safety switch.

Just curious if this is in the code anywhere so I know for future reference and to satisfy curiosity.


PS: As I was typing this I came across NEC 430.105. Pretty sure its legal...
 

jap

Senior Member
Occupation
Electrician
I never break a neutral in a disconnect.

JAP>
A friend of mine called me for some help to wire a safety switch (Pull out type) that powers a 120v pool pump (its an older pump).

Most of the safety switches say "240 volt" on the shelf, but there was a single one that said "120/240". He bought that one but called me first. I never really seen a safety switch labeled as 120/240 so I asked him to open it to see if there was a neutral bus isolated from the case and ground bus but it was sealed so couldn't open it.

I started to look into the code to see if this was mentioned but couldn't find anything. With that said, I don't see why it wouldn't work to just hook up the incoming neutral to the "Load" and the neutral to the pump on the "Line" terminal.

There's a single copper plate that connects the loads and the pull out is designed to disconnect everything simultaneously, even if you were to pull at an angle. Essentially it can only be inserted directly straight into the safety switch.


Just curious if this is in the code anywhere so I know for future reference and to satisfy curiosity.


PS: As I was typing this I came across NEC 430.105. Pretty sure its legal...


And why would you want to do that?

JAP>
 

Npstewart

Senior Member
He ended up installing a motor rated toggle switch. The question is just so I know for the future, and because im curious why they make and advertise a safety switch rated for 120/240 if you cannot use it for 120v, unless you switched the neutral.
 

jap

Senior Member
Occupation
Electrician
I wouldn't switch the neutral at all.

Was just questioning landing the incoming neutral on the load and the neutral to the pump on the line.

JAP>
 

retirede

Senior Member
Location
Illinois
He ended up installing a motor rated toggle switch. The question is just so I know for the future, and because im curious why they make and advertise a safety switch rated for 120/240 if you cannot use it for 120v, unless you switched the neutral.

You are not required to switch the neutral. What leads you to think otherwise?
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
You could wire it to switch the neutral as it would disconnect at the same time as the hot. You could also just tie the neutrals together and just put the hot line/load on the disconnect.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
May not b the case in his switch but I note in some manufacturer catalogs a switch with a 120/240 rating has a neutral bar (isolated) where as the switches with a 240 rating (only) have no neutral bar.
 

jap

Senior Member
Occupation
Electrician
I was always taught, "Though shall not switch the neutral unless specifically required to".

Jap>
 

xformer

Senior Member
Location
Dallas, Tx
Occupation
Master Electrician
May not b the case in his switch but I note in some manufacturer catalogs a switch with a 120/240 rating has a neutral bar (isolated) where as the switches with a 240 rating (only) have no neutral bar.
Cant all electric equipment rated for 240V be used on systems of less than 240V? I know this could be a waste of money but isnt is allowed?
 

jap

Senior Member
Occupation
Electrician
Cant all electric equipment rated for 240V be used on systems of less than 240V? I know this could be a waste of money but isnt is allowed?

I think it may be an option offered to get it with or without an insulated neutral bar.

Jap.
 

jap

Senior Member
Occupation
Electrician
MWBC would be the main reason, otherwise switching the hot and neutral at the same time should not be an issue.

Switching the neutral is not common practice.

Not even on a MWBC.

Oh well,,, to each his own.

Jap>
 

jap

Senior Member
Occupation
Electrician
It is not a common practice. Especially not on a MWBC.

Disconnecting both leads to the OPs motor will not cause an issue of any kind.

Are you saying most are disconnecting the neutral on MWBC's ?

I beg to differ.

Jap>
 

jap

Senior Member
Occupation
Electrician
I'd rather someone default to never switching a neutral, and, only switch a neutral when it is required to be switched.

Rather than switch a neutral as their common practice when there is no need or reasoning to do so.

Jap>
 