For a 120/240v, 4 wire, three phase service, can i get three pole breakers that can serve three phase loads? How does this three phase service work?
 

kingpb

Senior Member
Location
SE USA as far as you can go
Occupation
Engineer, Registered
cvirgil467 said:
For a 120/240v, 4 wire, three phase service, can i get three pole breakers that can serve three phase loads? How does this three phase service work?

a 120/240V system as stated, is a single phase three wire system. Please correctly restate the voltage you are describing so we can ensure the best answer to your question.

If what you meant is a 240/120 V delta system, then yes, you can run three phase loads from this system using 3 pole breakers.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
Sounds like a delta secondary, with 240 volts from phase to phase, and with one phase having a grounded center tap. That gives you 120 volts phase to ground (available only from the winding that has the center tap). You can use a three phase breaker to serve a 3-phase 240 volt load.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
This commonly called a 4 wire Delta service which would have a center tap on one of the transformer winding.
 