I'm working on a remodel where the previous electrician run a 10/2/2 MC for a 120 lighting circuit and a 277 circuit. I know you can run both in a conduit but is it ok to use MC?
Why not? If you can do it in conduit I can see no reason not to in MC as long as the color phasing is done.I'm working on a remodel where the previous electrician run a 10/2/2 MC for a 120 lighting circuit and a 277 circuit. I know you can run both in a conduit but is it ok to use MC?
From which panel?what about sharing the neutrals from two different sources, or the grounding?
what about sharing the neutrals from two different sources, or the grounding? are you saying a 10 awg/then 2#2 awg wires in the same MC cable? never seen a 10/2/2 cable, doesn't sound code compliant to me?![]()
biggest problem i see is we need a gray for 277 and a white for the 120 and not sure they can not be taped .
It sure is a bad idea but if you can get past the marking part then for lack of a " shall not" i guess it would fly
what about sharing the neutrals from two different sources, or the grounding? are you saying a 10 awg/then 2#2 awg wires in the same MC cable? never seen a 10/2/2 cable, doesn't sound code compliant to me?![]()
biggest problem i see is we need a gray for 277 and a white for the 120 .
Jim, can you point us to this requirement?
Roger
I haven't seen it either but I learned on this forum a year or so ago that it is available. Basically there are two 2 wire circuits available in the mc as Trevor stated.never seen a 10/2/2 cable,