Can 120 and 277 volt lighting circuits from 2 different panels be routed thru the same low-voltage relay panel?

Is there a code violation having different voltages from different sources within the same enclosure. Neither circuit is connected to an emergency system.

Thanks!
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Sparky5150 said:
Is it possible for Article 404.8 B to apply?


404.8(B) applies to snap switches. The OP makes no mention of adjacent snap switches so I would say that it does not apply.
 

haskindm

Senior Member
Location
Maryland
I don't believe that even the most creative interpretation would classify a relay panel as a "snap switch", so I can't see how 404.8 can apply. If you are installing snap switches then barriers may need to be installed.
 
Thanks for the replies! I just needed to know if there were any other references in the code similar to 404 regarding seperation of voltage, but I guess not.

If there were enough 120 volt circuits in the building that needed to be controlled by relays I would add an additional relay panel, but there are only 3 120 volt circuits. I will run them thru the same relay panel as the 277 volt circuits.
 

rzuffi

Member
I know for a fact that Lutron has switching panels that accept 120/277/347/220-240V in their Softswitch512 line.
 