I imagine if I search hard enough I could find this mentioned on the forum but something came up that is a subtle nuance in the wording of 2017 705.12(B)(2)(3)(b) that did make me pause for a moment and wonder what everyone else's thoughts are:
"...the sum of 125% of the power source(s) output circuit current and the rating of the overcurrent device protecting the busbar shall not exceed 120%..."
I've interpreted that as a fail if either condition is not met -> an example of how you could pass the breaker test but fail the 125% would be using a 100% rated breaker.
It was recently posed to me that because overcurrent device is not pluralized, the intention is 125% of the PV source circuit (or other onsite parallel power source) plus the rating of the main breaker. Has anyone else ever thought this? Example of why this would make a difference:
200kW of PV
400A main 480V, 3PH
400A OCPD---[600A Panel]---301A of PV = 701A (less than 720A from 120% rule)
However, it would be installed as;
400A OCPD---[600A Panel]---350A OCPD (301A of PV next size up) = 750A (120% fail)
Thoughts?
Regards,
Steve
I imagine if I search hard enough I could find this mentioned on the forum but something came up that is a subtle nuance in the wording of 2017 705.12(B)(2)(3)(b) that did make me pause for a moment and wonder what everyone else's thoughts are:
"...the sum of 125% of the power source(s) output circuit current and the rating of the overcurrent device protecting the busbar shall not exceed 120%..."
I've interpreted that as a fail if either condition is not met -> an example of how you could pass the breaker test but fail the 125% would be using a 100% rated breaker.
It was recently posed to me that because overcurrent device is not pluralized, the intention is 125% of the PV source circuit (or other onsite parallel power source) plus the rating of the main breaker. Has anyone else ever thought this? Example of why this would make a difference:
200kW of PV
400A main 480V, 3PH
400A OCPD---[600A Panel]---301A of PV = 701A (less than 720A from 120% rule)
However, it would be installed as;
400A OCPD---[600A Panel]---350A OCPD (301A of PV next size up) = 750A (120% fail)
Thoughts?
Regards,
Steve