There is a great thread discussion on sizing of OCPD and panelboards, etc. here:
https://forums.mikeholt.com/threads/80-rule.2556309/post-2611803
The MilBank spec sheet for U224MTBPL (200A panel) stated "200 amps continuous" .
The Siemens spec sheet for MC2440B1200CE says 200 amps continuous duty
Does "continuous" mean that the busbar is, in fact, rated for 200 amps continuous ?
In other words, is it permitted for five continuous 40 amp branch circuits to pull 200 A?
Or is the calculated load not supposed to exceed 160 amps?