- Location
- Southern California
I am trying to backfeed 200A of PV on 400A and 600A panels with a switchboard without derating the panel. For example, on a 400A panel with a 4 breaker location switchboard, I have two 200A breakers feeding two subpanels. I want to install a 200A PV backfeed breaker on the third breaker position and disable the fourth breaker location, or note that no additional loads be put on the switchboard. This would prevent the instance of any draw on the panel being larger than 400A regardless of utility or PV production sources. We're simply trying to prevent the main bus from seeing a current of >120% of the bus rating, right? This can be achieved via the 120% rule on production sources but can also be achieved by limiting the maximum possible load on the bus to 120% of the bus rating, that is, to limit the sum of all breakers to 120% or less. We do this with load relocation situations on 100A and 200A panels, shouldn't it work here.