We are installing a dual inverter system w/ battery BU. We were unsure how this should be wired to the SE BU interface (transfer switch) so SE sent me this diagram attached. The flow from inverters back to the MSP seems straight forward but it raised several ?s about the infamous 120% rule and having the "other power source" (aka solar) breaker on a subpanel and not in the MSP. Any help clearing this up would be appreciated. My questions are:
1 - Since they are using passthrough lugs on the feeder to the BU subpanel "C", which passes through the transfer switch to the 200A main on the subpanel at "B", does the 120% rule apply to the MSP? If so how, since there is no solar breaker attached to the MSP to calculate?
2 - Is subpanel "C" subject to the 120% rule itself? It's not Service Equipment but it is on the load side of the Service Disconnect, and per 705.12B.2.3.b has both a "primary source" and "another power source at the opposite end". So what's the rule for that?
3 - In the inverter combiner panel on the right, is the breaker at "D" necessary? Can't this panel be MLO or does the production meter in between make a difference? The meter is not a "load" correct?
1 - Since they are using passthrough lugs on the feeder to the BU subpanel "C", which passes through the transfer switch to the 200A main on the subpanel at "B", does the 120% rule apply to the MSP? If so how, since there is no solar breaker attached to the MSP to calculate?
2 - Is subpanel "C" subject to the 120% rule itself? It's not Service Equipment but it is on the load side of the Service Disconnect, and per 705.12B.2.3.b has both a "primary source" and "another power source at the opposite end". So what's the rule for that?
3 - In the inverter combiner panel on the right, is the breaker at "D" necessary? Can't this panel be MLO or does the production meter in between make a difference? The meter is not a "load" correct?