I am new to this forum and have plundered throughout the forum looking for a clear answer to this. (If there is a thread that answers please direct me to it)
So here we go.
I am working on coming up with a solution for this Main Panel which I see quite frequently in my area. I am attaching a photo of the spec sheet.
Square D Meter Main (Newer looking) SC12L200F. One note on the panel says "TOTAL CIRCUIT BREAKER HANDLE RATING NOT TO EXCEED 140A PER CIRCUIT CONNECTOR". I have seen that the six handle rule would apply instead of the 120% rule but we keep coming across an issue with how we calculate the maximum solar backfeed on this panel and how the Bus Bar would play into it. My understanding is that if the panel has an up stream OCPD we would use that into the 120% rule calcs. This panel does not (unless the meter counts, hence "Meter Main"?) but we want to make sure that 1. We are not Frying the Busbar and 2. We are following all codes associated with these types of panels.
So the question is, for this panel "Mains 200A Max" what is the maximum amount of Solar Backfeed can be on this panel that follows NEC 2017 and will not do anything harmful to the main panel.
I am new to this forum and have plundered throughout the forum looking for a clear answer to this. (If there is a thread that answers please direct me to it)
So here we go.
I am working on coming up with a solution for this Main Panel which I see quite frequently in my area. I am attaching a photo of the spec sheet.
Square D Meter Main (Newer looking) SC12L200F. One note on the panel says "TOTAL CIRCUIT BREAKER HANDLE RATING NOT TO EXCEED 140A PER CIRCUIT CONNECTOR". I have seen that the six handle rule would apply instead of the 120% rule but we keep coming across an issue with how we calculate the maximum solar backfeed on this panel and how the Bus Bar would play into it. My understanding is that if the panel has an up stream OCPD we would use that into the 120% rule calcs. This panel does not (unless the meter counts, hence "Meter Main"?) but we want to make sure that 1. We are not Frying the Busbar and 2. We are following all codes associated with these types of panels.
So the question is, for this panel "Mains 200A Max" what is the maximum amount of Solar Backfeed can be on this panel that follows NEC 2017 and will not do anything harmful to the main panel.