120 volt duplex receptacle with the link split has 2 circuits feeding it with different phases and a common neutral.
Is this acceptable per the NEC
120 volt duplex receptacle with the link split has 2 circuits feeding it with different phases and a common neutral.
Is this acceptable per the NEC
Common trip would only be required for phase to phase loads. If there are only phase to neutral loads (as they would have to be from a split duplex receptacle) then common manual operation is good enough.Yes it is OK provided you use a common trip circuit breaker.
Common trip would only be required for phase to phase loads. If there are only phase to neutral loads (as they would have to be from a split duplex receptacle) then common manual operation is good enough.
The OP said "common neutral", I take that to mean this is a MWB set up. Common trip required, yes?
210.4 Multiwire Branch Circuits.
(B) Disconnecting Means. Each multiwire branch circuit
shall be provided with a means that will simultaneously
disconnect all ungrounded conductors at the point where
the branch circuit originates.
Informational Note: See 240.15(B) for information on the
use of single-pole circuit breakers as the disconnecting
means.
240.15 Ungrounded Conductors.
(B) Circuit Breaker as Overcurrent Device. Circuit breakers
shall open all ungrounded conductors of the circuit both
manually and automatically unless otherwise permitted in
240.15(B)(1), (B)(2), (B)(3), and (B)(4).
(1) Multiwire Branch Circuit. Individual single-pole circuit
breakers, with identified handle ties, shall be permitted
as the protection for each ungrounded conductor of multiwire
branch circuits that serve only single-phase line to neutral
loads.
If it is not a MWBC, then consider the following:
210.7 Multiple Branch Circuits. Where two or more branch circuits supply devices or equipment on the same yoke or mounting strap, a means to simultaneously disconnect the ungrounded conductors supplying those devices shall be provided at the point at which the branch circuits originate.
From 2011
If I use a handle tie on two single pole breakers and one trips, is the handle movement sufficient to trip the other?
a means that will simultaneously disconnect all ungrounded conductors at the point where the branch circuit originates
I agree with most of what has been said so far, and want to add this is one reason the removable link is there in the first place. Even if there were such a beast as a three plex receptacle (maybe there is), you could have one common neutral and all three phases of a three phase system powering each of the three "ports".120 volt duplex receptacle with the link split has 2 circuits feeding it with different phases and a common neutral.
Is this acceptable per the NEC