S symo64 New member Aug 19, 2004 #1 IS A SEPERATE NO. 8 GROUND WIRE REQUIRED FROM POOL LITES TO GROUND BAR IN ELECTRICAL PANEL IF NON METALLIC CONDUIT IS USED?
IS A SEPERATE NO. 8 GROUND WIRE REQUIRED FROM POOL LITES TO GROUND BAR IN ELECTRICAL PANEL IF NON METALLIC CONDUIT IS USED?
electricman2 Senior Member Location North Carolina Occupation Retired Electrical Contractor Aug 19, 2004 #2 Re: 120 VOLT POOL LITES No. It just has to be sized in accordance with table 250.122 but be not smaller than No. 12. The No. 8 is required in non-metallic conduit between the junction box and forming shell of wet-niche fixtures.
Re: 120 VOLT POOL LITES No. It just has to be sized in accordance with table 250.122 but be not smaller than No. 12. The No. 8 is required in non-metallic conduit between the junction box and forming shell of wet-niche fixtures.