Re: 120 volts 277 volts

I have never seen a 4 square box equipped with a permanent barrier for this purpose. Do they make such a thing?
 
Re: 120 volts 277 volts

Bryan, we use them quite often to seperate Critical and Normal power switches in the same box.

They are used with two gang plaster rings and are made in plastic and metal.

Roger
 
Re: 120 volts 277 volts

Oh yeah they make them, we use them when we have more than 1 phase of 277 lighting in a switch box.

Question, with a 120 and a 277 circuit in a box is there always more than 300 volts between switches or just when we have different phases?

I am thinking with 120 and 277 volt circuits both from the same phase you would only have 157 volts between switches. Is this a correct assumption?
 
Re: 120 volts 277 volts

120 volts and 277 volts are derived from two different sources. They are both in reference to ground. They are allowed to occupy the same enclosure without a barrier. (less than 300v between energized conductors) However neutrals, if present, must be indentified differently to indicate they are from two different sources.
 
Re: 120 volts 277 volts

derwith,
Since both the 120 and 277 volt systems are referenced to a common point, there is voltage between the systems ungrounded conductors. The voltage between A phase on the 120 volt system and B or C phase on the 277 volt system is ~359 volts.
Don
 
Re: 120 volts 277 volts

Don,

Both the neutral of the 120 volt system and the neutral of the 277 volt system are at ground potential. There is 120 volts to ground and there is 277 volts to ground. 120 minus 277 is 157. That is the maximum difference between ungrounded conductors.

The 120 volt to ground circuit has either 240 volts single phase or 208 volts if three phase between ungrounded conductors. The 277 volt to ground circuit has 480 volts three phase between ungrounded conductors. It is 277 volts to ground whether using phase A, B, or C.

With a box containing two switches and one is 120 volts and the other is 277 volts, two 480 volt between ungrounded conductors would not be there.

I believe the 300 volt limitation is specifically to allow 277 volt switching.
 
Re: 120 volts 277 volts

derwith,
If you want to find the actual voltage between the A phase of the 120 volt system and the B phase of the 277 volt system you must use vector addition because these two votlages (vectors) are 120? out of phase. The 157 volt difference only applies when the 120 and the 277 voltages are both of the same phase. Any time there is a combination of phases, the voltage between the two will be ~359 volts and require a barrier per 404.8(B).
Don
 
Re: 120 volts 277 volts

I always wondered what that slot in the plaster ring was for. :eek:

johnston17.gif
 
Re: 120 volts 277 volts

Originally posted by bphgravity:
I always wondered what that slot in the plaster ring was for. :eek:
They are also used to satisfy 725.55 for seperation of line voltage and low voltage. If you notice, plastic boxes have them as well.
 
Re: 120 volts 277 volts

Don,

My math and logic of the previous post is wrong. Thanks for pointing that out Don.

Here is another thought. Since there are two separately derived systems wouldn't there be no voltage between them except for incidental capacitance and inductance from the wiring system?

Wouldn't this would be true regardless if the systems are single phase or three phase.
 
Re: 120 volts 277 volts

derwith,
While they are separate systems, they share a common reference point...the grounding electrode system. This common reference point resutls in a voltage between the ungrounded conductors of the two different systems.
Don
 
Re: 120 volts 277 volts

Hi Don,

You are right in regards to the voltages of both systems to ground. What about the voltage on the ungrounded conductor of one system to the voltage on the ungrounded conductor of the other system?

How are they referenced together?
 
Re: 120 volts 277 volts

derwith,
Because XO of both transformers are tied together. Draw two wye connected transformers and connect the center point of the two wyes, then look at the current path. It is from the ungrounded conductor of one transformer, to the grounded conductor of that transformer, to the grounded conductor of the second transformer, to the ungrounded conductor of that second transformer.
Don
 
Re: 120 volts 277 volts

Hi Don,

As they say: a picture is worth a thousand words. The relationship is obvious to me now, including the 120 degree vectoring.

Thank you very much.