Hello All - I was taking a quick online quiz and for the question below I got the answer wrong b/c I used 240V instead of 120V which gave me a 3% Vdrop of 7.2V @ 240V instead of 3.6V @ 120V. The question says the source power is 120/240 but the loads described to engineer the circuit are all 240 and the current used in the formula is produced "at 240". It's also odd the explanation says 3V is the maximum when it's actually 3.6V and this is also the only indication the author used 120V since it says in explanation "3V maximum"
So am I correct to use 240 or is 120 correct and if so why? It's actually not the only answer I questioned out of 20 sample questions and before I purchase the entire book I want to make sure it's accurate info.
You need to install a feeder to a subpanel in a newly constructed remote workshop at a single family dwelling. The source power is 120/240V single phase. The load in the workshop is engineered to be 85 amperes continuous at 240V, and a non-continuous 240V load of 35 amperes. The wire length will be 245' from the main service termination point to the workshop termination point. Using the Informational notes in Article 215 and the following formula, size the THWN copper feeder wires to provide reasonable efficiency of operation by preventing excessive voltage drop (keeping the wires as small as possible). The formula is: VD = 2 x L x R x I ÷ 1000. VD = voltage drop, L = length, R = resistance in /1000'.
answer choices: a: 1/0 b: 4/0 c: 350kcmil d: 500kcmil (350kcmil is shown as the correct answer, see below)
explanation given:
215.2(A)(1)(a,b) directs the load to be calculated as follows: 35A @ 100%, 85A @ 125%. 35 x 106.25 = 141.25A. Inf. note 2 shows the need to maintain the voltage drop to less than 3%. The wire resistance is found in Ch. 9 Table 8, and the wire ampacity is from Table 310.15(B)(16). Using the resistance from #350 kcmil: 2 x 245' x 0.0382 x 141.25A = 2643.9175 ÷ 1000 = 2.643V, just under the 3V maximum.
So am I correct to use 240 or is 120 correct and if so why? It's actually not the only answer I questioned out of 20 sample questions and before I purchase the entire book I want to make sure it's accurate info.
You need to install a feeder to a subpanel in a newly constructed remote workshop at a single family dwelling. The source power is 120/240V single phase. The load in the workshop is engineered to be 85 amperes continuous at 240V, and a non-continuous 240V load of 35 amperes. The wire length will be 245' from the main service termination point to the workshop termination point. Using the Informational notes in Article 215 and the following formula, size the THWN copper feeder wires to provide reasonable efficiency of operation by preventing excessive voltage drop (keeping the wires as small as possible). The formula is: VD = 2 x L x R x I ÷ 1000. VD = voltage drop, L = length, R = resistance in /1000'.
answer choices: a: 1/0 b: 4/0 c: 350kcmil d: 500kcmil (350kcmil is shown as the correct answer, see below)
explanation given:
215.2(A)(1)(a,b) directs the load to be calculated as follows: 35A @ 100%, 85A @ 125%. 35 x 106.25 = 141.25A. Inf. note 2 shows the need to maintain the voltage drop to less than 3%. The wire resistance is found in Ch. 9 Table 8, and the wire ampacity is from Table 310.15(B)(16). Using the resistance from #350 kcmil: 2 x 245' x 0.0382 x 141.25A = 2643.9175 ÷ 1000 = 2.643V, just under the 3V maximum.