I am new to this forum, I have looked at the previous posts, but could not find the answer to the following questions:
In regards to NEC 230.95 Requirements, is a service protected by a 1200 A (MCCB) breaker required to have GFP? Part of my confusion arises from the fact that I believe that this breaker could not have a trip plug of more than 960 A...assuming a regular as opposed to a 100% rated breaker
Along the same lines if I am deriving a service from a 750 KVA utility-owned trasformer, and my intend is to size this conductors to deliver the FLC of the transformer, ~ 902 A. Would this set of conductors considered to be a 1000 A or more service in regards to 230.95...? i.e. 902 * 1.25 = 1128 A
I should mention that questions 1 and 2 are two separate instances...
Best regards
In regards to NEC 230.95 Requirements, is a service protected by a 1200 A (MCCB) breaker required to have GFP? Part of my confusion arises from the fact that I believe that this breaker could not have a trip plug of more than 960 A...assuming a regular as opposed to a 100% rated breaker
Along the same lines if I am deriving a service from a 750 KVA utility-owned trasformer, and my intend is to size this conductors to deliver the FLC of the transformer, ~ 902 A. Would this set of conductors considered to be a 1000 A or more service in regards to 230.95...? i.e. 902 * 1.25 = 1128 A
I should mention that questions 1 and 2 are two separate instances...