Had a 1200 amp 3 phase Sq D Main trip for a complex. 24 - 125 amp 1ph services and 1 - 400 amp house panel 3 phase.
Breaker would not clear on first attempt. Had to shut down all breakers and I think it cleared it but cant figure out why it tripped. To reset a 1200 amp 3 phase
Note I took apart and removed all meters to inspect, Due to the shearbolts not broken off. Checking for other flaws found none.
Is this normal procedure to shut down all main. Wasn't I inspected the whole cabinet. 1 screw in meter stack may have rubbed thru but no evidence of arc flash.
Question 1 Not sure if screw penetrated. But after all breakers were shut off. I was able to reset 1200 amp main. Then gradually restore in sequences of 4. Until all 25 were engaged. All was good. Did I need to shut off all breakers to reset this type of breaker?
Question 2 Shearbolts in meter stack. Whomever installed this service did not break off the shearbolt. Problem it can cause. I did not attempt to do this unless owner seen and asked to do so. Overall work looked ok from whomever installed. But this was red flag.
What can a non shearbolt do.. I did not check torque, Been on for 3 years plus.
Question 3. 400 amp 3 phase 208 main for house panel in busbar tap. They paralleled 2 - sets of 250 KCM alumin. But problem is they installed in 1 -4in conduit. Instead of separate Paralleled conduits.
Can the Increase of Magnetics (Ripple effect) Trigger this breaker to open.?
Question 4 It was in the blizzard. And all were home. Electric dryers., Gas stove. Electric water heaters. Could everyone have been stuck in home and used the dryer and washers with water heat demand. And exceed the Diversity of the load calcs? Any comments ?
Breaker would not clear on first attempt. Had to shut down all breakers and I think it cleared it but cant figure out why it tripped. To reset a 1200 amp 3 phase
Note I took apart and removed all meters to inspect, Due to the shearbolts not broken off. Checking for other flaws found none.
Is this normal procedure to shut down all main. Wasn't I inspected the whole cabinet. 1 screw in meter stack may have rubbed thru but no evidence of arc flash.
Question 1 Not sure if screw penetrated. But after all breakers were shut off. I was able to reset 1200 amp main. Then gradually restore in sequences of 4. Until all 25 were engaged. All was good. Did I need to shut off all breakers to reset this type of breaker?
Question 2 Shearbolts in meter stack. Whomever installed this service did not break off the shearbolt. Problem it can cause. I did not attempt to do this unless owner seen and asked to do so. Overall work looked ok from whomever installed. But this was red flag.
What can a non shearbolt do.. I did not check torque, Been on for 3 years plus.
Question 3. 400 amp 3 phase 208 main for house panel in busbar tap. They paralleled 2 - sets of 250 KCM alumin. But problem is they installed in 1 -4in conduit. Instead of separate Paralleled conduits.
Can the Increase of Magnetics (Ripple effect) Trigger this breaker to open.?
Question 4 It was in the blizzard. And all were home. Electric dryers., Gas stove. Electric water heaters. Could everyone have been stuck in home and used the dryer and washers with water heat demand. And exceed the Diversity of the load calcs? Any comments ?