1200 amp main 120/208 3 phase

Status
Not open for further replies.

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
I believe per 230.95 I do not need a 1200amp 120/208v main disconnect with ground fault protection. Being as voltage is 120v per phase to ground.
Am I missing something here? I received some conflicting feedback.
 

jap

Senior Member
Occupation
Electrician
I believe per 230.95 I do not need a 1200amp 120/208v main disconnect with ground fault protection. Being as voltage is 120v per phase to ground.
Am I missing something here? I received some conflicting feedback.

I believe you're correct.

Jap>
 

jap

Senior Member
Occupation
Electrician
Thank you I thought I perhaps missed an exception been wrong before many times.

And where that rule does apply It starts at "1000 amps or more", not to be confused with thinking that it starts at "more than 1000 amps".

JAP>
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Being as voltage is 120v per phase to ground.
Am I missing something here?
You're correct it is not required because you're voltage to ground does not exceed 150 volts. If you have a 480Y/277 volt system the voltage to ground would exceed 150 volts.
 