hillbilly1
Senior Member
- Location
- North Georgia mountains
- Occupation
- Owner/electrical contractor
The start contact on two wires, are dry contacts, so you can parallel as many as you want. The control voltage comes from the generator.
When I have put two ATSs on a Generac, the instructions showed how to wire them as a master/slave pair.
There is more to it than, the cheapest generator that will get you 130 or whatever kw you want. Who is going to service it going forward and are they any good at servicing the product would be question #1.
OP needs to figure out the load, but I'm guessing 1200 A is way overkill.
Yes and no, if you use a service rated transferswitch, it can have a lower rating, such as 800 amps, the 1200 amp can remain. Another issue if you go with a bigger generator and 8 transfer switches, you will need a distribution panel off the generator feed.They have hired me to perform a load Calc.
But regardless of the actual load, if it has a 1200A main, then a single transfer switch will need to be a 1200A.
And there are 8, 200 amp subs, so regardless of actual usage, separate transfer switches to power the entire facility will have to be 200A switches.
Apologies for not having paid attention to all the facts in this case.
Nevertheless, all generators of this size should be able to do 2 wire start. If it is a true industrial unit, it may be that the Generac house is the only one that can ever have the keys to work on it, and the customer may be out of luck and have to pay whatever they ask. That's how it is in my territory.
Looking at the standard commercial line, I don't see any transfer switches over 800 amps, so you probably have to go to the industrial dealer to buy a 1600 amp version, and then you will be locked into their service forever. So it probably makes more sense to go with ASCO whatever you decide to do.
Not really. For the case of a a non-service rated transfer switch, you could downsize that 1200 main to something smaller. But note you might not even need to do that. There is no requirement that a switch be protected at its rating by an ocpd. What you will have to do is meet the withstand and sccr ratings of the switch. The manufacturer will give you a chart of different breakers with different ratings and they typically allow you to have a bigger breaker than the switch rating in some cases.They have hired me to perform a load Calc.
But regardless of the actual load, if it has a 1200A main, then a single transfer switch will need to be a 1200A.
And there are 8, 200 amp subs, so regardless of actual usage, separate transfer switches to power the entire facility will have to be 200A switches.
Yes and no, if you use a service rated transferswitch, it can have a lower rating, such as 800 amps, the 1200 amp can remain. Another issue if you go with a bigger generator and 8 transfer switches, you will need a distribution panel off the generator feed.
Until you know loads, it's all guess work. Like I said, I've got a 600 xfer switch that has like 8 200A panels and 5 100 A panels spread across 3 buildings, and load is only about 320A. Just saying loads could be a lot less than you think.If I went the 8 separate route, I was planning to use a can, and install terminal blocks inside, and make use of tap rules to feed the ATSs.
Hope for a big electrical room! LOL!If I went the 8 separate route, I was planning to use a can, and install terminal blocks inside, and make use of tap rules to feed the ATSs.
If I may nitpick your wording: you have one service. You have 9 meters.I am working with a customer on a building right now that has 9, 480V, 100 or 200A services grouped, with a 1000 or 1200A pre-meter switch, although they occupy the whole building as one. Was once set up for tenants. They are running a huge laser cutter, press brakes, and have some huge AC planned in the future, nevertheless you could almost run the whole building off a single 200A 480V service from our observations.
Correct you are. Never thought of it that way I guess.If I may nitpick your wording: you have one service. You have 9 meters.