Oh ok, I misunderstood, thought it was just for connecting/disconnecting as the work was being done and switched over.There are emergency lug if the power goes out they can bring in a temp generator and hook to the MTS.
So why not make the MTS be your service disconnect, then you could eliminate the MB in P1. Although you have the pesky GFPE requirement so you couldn't use a standard switch, would have to go to a Pringle/BPS to get that functionality. Or maybe TJ has the best idea with the Kirk key.