memyselfandI
Senior Member
- Location
- Hampton Roads, Virginia
Here is one for everyone. I have an electrical contractor getting ready to install a 1200 A sub fed panel in an industrial facility. He said that he was going to install 3 sets of 500 MCM CU with a 3/0 CU ground with each set. As I looked at 310.16 and looked at the table, I noticed that three sets of 500 will only come to 1140 A according to the 75 degree column. When I mentioned this to him he said that he was using the 90 degree column for the circuit and that because it was a higher amperage rating that the overage was okay for a 1200 A breaker and that if he based it on the 75 deg column the next higher breaker rating is 1200 A anyway. I asked him if his connections were rated for 90 deg and he said no they are rated for 75 deg. I was under the assumption that he can use the 90 deg column for his wires, but if the terminations are only rated for 75 deg then the value of the conductors are only good for the value in the 75 deg column. To me the conductors for this circuit are not adequate for the OCP. It seems that he is sizing the breaker to the conductors and not the conductors to the breaker. Now we all know that there is no way that the circuit will pull 100% of the load, 110.14 C (b) if I interpret it right, is specific on the temperature limitation on connections when dealing with circuits of 100A or more. My question is this, is this acceptable practice to size the conductors in this manner or are there other provisions in the code that allow this?