I have a comm bldg with florescent lighting.With a load calculation I figure I need a 1200a capacity.The runs are figured to be run under ground from Main sw to txmfr pad .I figure w/flour ltgs the neutral is current carrying and I have to use this in my derating ( w/=80%).The feeders are to be run in pvc and no more than 4 cond per conduit.Which translates to me as(4-400kcm (90 deg.C) w/3/0 grnd wire in ea of the 4-3" pvc conduits.
Because the conduits are run underground , does this negate any of the derating rules.
Secondary runs are under 30 feet.(VD ok)
I welcome any opinion or any alternate approach to the project. Thank you.
Because the conduits are run underground , does this negate any of the derating rules.
Secondary runs are under 30 feet.(VD ok)
I welcome any opinion or any alternate approach to the project. Thank you.