Thank you sir!(5)x set of 1000 MCM AL in 4" PVC would be $273,000.00 + tax, and 1200/hrs labor.
(6)x set of 750 MCM AL in 3-1/2" PVC would be $241,000 + tax, and 1150/hrs labor.
That would include a quazite box mid-point for each run. This is for straight 480 not 480/277. VD calculated at <3% for 1000A load.
100% customer owned. A couple steps away from PocoWill this be before or after the POCO service point? That will affect the applicable sizing rules.
I agree with Larry look getting a quote from the power company would be prudent. You could do your own step up step down, #2 15kv CN is about $3.75/ft so about $12k for wire. Unfortunately transformers are going to be an arm and a leg and they're availability sucks right now - doubtful it would be worth it in at this length.
Yeah a real real quick look at eBay shows 15-30k is about the cheapest used 500kva to one Meg transformers go, so add in your primary wire you're at about the same bill for the four sets of 500 route. Then you have kind of a bastard system with older lossier transformers, two transformers of voltage drop, etc.....Thanks this was generally my thought as well as far as step up step down. Might be able to save a few shekels going that route, but transformers are not exactly cheap or anywhere close to readily available nowadays, so when you factor everything in, it could end up being a wash.
That took you all of five minutes to do when you know how to use your software and trust it....unlike most here(5)x set of 1000 MCM AL in 4" PVC would be $273,000.00 + tax, and 1200/hrs labor.
Energy codes aside, $100k can buy a lot of loss. Another place where you need to do the calcs.with older lossier transformers, two transformers of voltage drop, etc.....
correctThat took you all of five minutes to do when you know how to use your software and trust it....unlike most here
Just out of curiosity. Which software did you use?(5)x set of 1000 MCM AL in 4" PVC would be $273,000.00 + tax, and 1200/hrs labor.
Conest Intellibid.Just out of curiosity. Which software did you use?
Agreed. Not sure if you've priced transformers recently, but doing a step up-step down might not be that different in total cost.Holy smokes!!! Looks like you need a higher voltage. That's insane.
That's basically exactly what I did a few weeks ago when this came up. I said 250k for a sense of magnitude, and probably a range of 150-350k depending on specifics.I would just tell the guy a quarter of a million dollars as a rough order of magnitude estimate and make him understand that it is subject to all the vagaries of what you can get in the way of parts if you actually end up getting a job out of the estimate.