I am having a notoriously hard to finding a VFD for 120V (input and output) for 1HP motor. The VFD is for a roof exhaust fan. Is there any listed products out there recommended?
Why do you feel it's needed?I am having a notoriously hard to finding a VFD for 120V (input and output) for 1HP motor. The VFD is for a roof exhaust fan. Is there any listed products out there recommended?
https://www.grainger.com/product/DAYTON-Centrifugal-Downblast-Roof-4YU95I don't think I've ever seen a VFD on a single phase motor. Is this a capacitor start motor? What happens when the RPM drops and the starting switch closes? Those capacitors are not rated for continuous use
Mechanical engineer asked me to put a VFD on the plans for this existing exhaust fan lolWhy do you feel it's needed?
https://www.grainger.com/product/DAYTON-Centrifugal-Downblast-Roof-4YU95
This is the fan, it's existing. I don't think it's capacitor start but I could be wrong.
If I take out the single phase motor and replace it with 3-phase motor, I don't know if it will be compatible with this due to dimension. Dimensions of single phase and 3-phase is different, no?I don't think that one comes with a motor. It says to use between a 1/4 and a 1HP motor. No electrical specs listed. Just buy a 3 phase motor for it. Only one more conductor to run
Three phase motors are usually cheaper. Also simpler design and more reliable. No capacitor and no starting switch
BTW a single phase motor in that kind of size without a capacitor would be a very rare bird
If I take out the single phase motor and replace it with 3-phase motor, I don't know if it will be compatible with this due to dimension.
Allow me to ask differently: What do you want the motor to do differently than it would if directly powered?Is there any drive that that controls a 120V 1hp motor kinda like a VFD? Capacitor start friendly
I'll ask my mechanical engineer, all he said was to specify him a VFD for this fan. I think maybe he wants the fan to automatically run on low during certain times. This fan is on full blast right now 24/7.Allow me to ask differently: What do you want the motor to do differently than it would if directly powered?
No. The dimensions of a three phase motor and single phase match as long as they are the same frame size.If I take out the single phase motor and replace it with 3-phase motor, I don't know if it will be compatible with this due to dimension. Dimensions of single phase and 3-phase is different, no?
You can't slow down a cap start motor. You can slow down a Permanent Split Capacitor motor (PSC) but there is no reason to when you can just install a VFD and a three phase motor, or get a multi speed motor like TwoBlocked suggests.Is there any drive that that controls a 120V 1hp motor kinda like a VFD? Capacitor start friendly
I think then I might just call out for a 3-phase motor with VFD. A VFD has an interface to schedule speed of the motor at certain times which is useful. But if I was to get a multi-speed motor do I also have to hook that up to a VFD?No. The dimensions of a three phase motor and single phase match as long as they are the same frame size.
You can't slow down a cap start motor. You can slow down a Permanent Split Capacitor motor (PSC) but there is no reason to when you can just install a VFD and a three phase motor, or get a multi speed motor like TwoBlocked suggests.
But if I was to get a multi-speed motor do I also have to hook that up to a VFD?
If I get a multispeed motor, how can I program it to run at different speeds at different times automatically? Is it done with a time clock relay?9
No, but most of the two speed motors I see are for applications where the motor is in the airflow. That is how those motors are designed to be cooled. The ventilator you linked to is belt driven and does not have the motor in the airflow