I just received a large piece of equipment that is rated a 120V, 20A circuit. On the back, it has a 250V, 20A flanged L6-20P inlet, HBL2325. The manufacturer wires machines for either 120V or 208V, as requested by the end user, but uses the same plug on the back of all units. The manufacturer asks the end user to construct a cord that goes from an L6-20R cord connector to a 5-20p or L5-20P, depending on what receptacle type we have.
So, my questions are these:
1) Does putting an L6-20P inlet on a 120V piece of equipment meet NEC?
2) 2020 NEC Article 406.8, noninterchangeability, says that “receptacles, cord connectors, and attachment plugs shall be constructed such that receptacle or cord connectors do not accept an attachment plug with a different voltage or current rating from that for which the device is intended.” Does this apply to the equipment? Or just to the construction of the receptacles and plugs? If not, what article would apply?
3) This setup would allow someone to connect this to 208V, 20A power in the future, which is a safety hazard. What part of NEC should prohibit this?
4) If we make a cord that has L6-20R on one end and 5-20p on the other, someone could use this cord in the future to try to plug a 208V item in to a 120V receptacle. Does this cord violate NEC?
5) Is it allowable, even if a bad idea, to use L6-20 components on a 120V circuit because they have a higher voltage rating? It says 250V, but doesn't provide a minimum.
I really appreciate everyone's help. I have enjoyed finding answers to many questions on the forum over the years.
So, my questions are these:
1) Does putting an L6-20P inlet on a 120V piece of equipment meet NEC?
2) 2020 NEC Article 406.8, noninterchangeability, says that “receptacles, cord connectors, and attachment plugs shall be constructed such that receptacle or cord connectors do not accept an attachment plug with a different voltage or current rating from that for which the device is intended.” Does this apply to the equipment? Or just to the construction of the receptacles and plugs? If not, what article would apply?
3) This setup would allow someone to connect this to 208V, 20A power in the future, which is a safety hazard. What part of NEC should prohibit this?
4) If we make a cord that has L6-20R on one end and 5-20p on the other, someone could use this cord in the future to try to plug a 208V item in to a 120V receptacle. Does this cord violate NEC?
5) Is it allowable, even if a bad idea, to use L6-20 components on a 120V circuit because they have a higher voltage rating? It says 250V, but doesn't provide a minimum.
I really appreciate everyone's help. I have enjoyed finding answers to many questions on the forum over the years.