120v & 277v circuits in same conduit.

Status
Not open for further replies.

ctroyp

Senior Member
Re: 120v & 277v circuits in same conduit.

jemelectric:
See 300.3(C).
...all conductors shall have an insulation rating equal to at least the maximum circuit voltage applied to any conductor within the enclosure, raceway, etc.


Sorry overlooked the "emergency."

[ October 03, 2003, 08:48 AM: Message edited by: ctroyp ]
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Re: 120v & 277v circuits in same conduit.

What type of emergency system, is it a Article 700, 701 or 702 application?
Art 700 is the only article that has restrictions on "emegency' circuits with non emergency circuits.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: 120v & 277v circuits in same conduit.

Tom, I agree that we need to know the application, and along with the restrictions in 700, 517 also requires seperation if a health care facilty is involved.

Roger
 
Re: 120v & 277v circuits in same conduit.

Thanks for the feedback,
It is an emergency system in a middle school.
Diesel generator.
Jason
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Re: 120v & 277v circuits in same conduit.

We still don't have enough information. Is it a
Emergency system per Art 700
Legally required standby system per Art 701
Optionally required standby system per Art 702

Look at the scope in the beginning of each article.
And 120 - 277 circuits can be run in the same raceway, but only Art 700 requires separation between emergency and non emergency circuits.

Not all generators are "emergency" generators, that is why we need to know how it is used.
 