120v circuit
mannyb
Florida
when installing a 120v circuit could I use the gen feed wire from generator using the neutral and ground for battery charger and installing a single wire to for power?
Hmm. In theory, yes, as long as they're all in the same raceway, and you have OCP.
Code compliant, I'm dubious.
I keep reading that and I still don’t understand. ☹️ It’s been a long day.
Can you explain it again? I’m assuming you’re talking about a Kohler with a load side feed for a battery charger…..
Basically could I use the neutral and ground from generator feed and install a Single wire for the hot to complete a 120v circuit?
So tap the neutral and ground on the genset, and then run a hot from a panel, presumably on the house, to feed a general use receptacle outlet somewhere close to the generator?
That would be a violation of 300.3
Gen neutral and egc is supply from the gen to the house. Then a hot wire from the house panel to keep the battery charged using the gen neutral and egc (back fed).
I doubt it is legal
It sounds to me like you are asking if you can create a multiwire branch circuit from a current 2 wire 102 volt circuit. If so, as long as the 2 hots are different phases, you have a handle tie on the feeding breakers, and the neutral runs in the same conduit or cable as the hots, then yes.
Thanks. I knew It couldnt do it providing the NEC address really made it clear. Thanks