when installing a 120v circuit could I use the gen feed wire from generator using the neutral and ground for battery charger and installing a single wire to for power?
 
when installing a 120v circuit could I use the gen feed wire from generator using the neutral and ground for battery charger and installing a single wire to for power?
Hmm. In theory, yes, as long as they're all in the same raceway, and you have OCP.

Code compliant, I'm dubious.
 
when installing a 120v circuit could I use the gen feed wire from generator using the neutral and ground for battery charger and installing a single wire to for power?

I keep reading that and I still don’t understand. ☹️ It’s been a long day.

Can you explain it again? I’m assuming you’re talking about a Kohler with a load side feed for a battery charger…..
 
I keep reading that and I still don’t understand. ☹️ It’s been a long day.

Can you explain it again? I’m assuming you’re talking about a Kohler with a load side feed for a battery charger…..
Basically could I use the neutral and ground from generator feed and install a Single wire for the hot to complete a 120v circuit?
 
So tap the neutral and ground on the genset, and then run a hot from a panel, presumably on the house, to feed a general use receptacle outlet somewhere close to the generator?


That would be a violation of 300.3
 
Gen neutral and egc is supply from the gen to the house. Then a hot wire from the house panel to keep the battery charged using the gen neutral and egc (back fed).

I doubt it is legal
 
Basically could I use the neutral and ground from generator feed and install a Single wire for the hot to complete a 120v circuit?
It sounds to me like you are asking if you can create a multiwire branch circuit from a current 2 wire 102 volt circuit. If so, as long as the 2 hots are different phases, you have a handle tie on the feeding breakers, and the neutral runs in the same conduit or cable as the hots, then yes.
 
So tap the neutral and ground on the genset, and then run a hot from a panel, presumably on the house, to feed a general use receptacle outlet somewhere close to the generator?


That would be a violation of 300.3
Thanks. I knew It couldnt do it providing the NEC address really made it clear. Thanks
 