AJElectric
Member
- Location
- Iowa
- Occupation
- Electrical Contractor, instrumentation and controls integration
Two separate buildings one with a 600A 277/480V service and other with a 800A 277/480 service. Each has a 120/208 transformer & panel for lighting/convenience/etc. circuits.
A 120V-fed PLC control panel and operator interface in building "A" controls equipment in both buildings. Remote I/O and operator interface in building "B" via ethernet comm. Provisions are in place for both an ethernet run and a 120V control circuit from main PLC over to remote panel in building B with the expectation that both control panels (in separate buildings) utilize the same 120V circuit. Automation contractor suggested this, but isn't necessarily "specifying" it.
I don't get a warm fuzzy doing this. Mostly because the neutral bonded at both services, my EGC for 120V circuit grounded at both ends, would create a parallel path for the neutral from one main service to the other (both also having neutral connection to POCO transf.) Any input on how to do this correctly, if it's even possible?
A second question is about the ethernet comm. between facilities. Are ethernet ports typically electrically isolated from power circuits of electronic/PLC/hub/etc? How can it be that this cable wouldn't be a current path from one building to another? Does TELCO usually have some type of isolator at each building it serves and would we need to implement something like that here?
A 120V-fed PLC control panel and operator interface in building "A" controls equipment in both buildings. Remote I/O and operator interface in building "B" via ethernet comm. Provisions are in place for both an ethernet run and a 120V control circuit from main PLC over to remote panel in building B with the expectation that both control panels (in separate buildings) utilize the same 120V circuit. Automation contractor suggested this, but isn't necessarily "specifying" it.
I don't get a warm fuzzy doing this. Mostly because the neutral bonded at both services, my EGC for 120V circuit grounded at both ends, would create a parallel path for the neutral from one main service to the other (both also having neutral connection to POCO transf.) Any input on how to do this correctly, if it's even possible?
A second question is about the ethernet comm. between facilities. Are ethernet ports typically electrically isolated from power circuits of electronic/PLC/hub/etc? How can it be that this cable wouldn't be a current path from one building to another? Does TELCO usually have some type of isolator at each building it serves and would we need to implement something like that here?