ryan_618 Senior Member Location Salt Lake City, Utah Sep 29, 2005 #2 Re: 120V Duplex Receptacles on 30A Breaker? What is the ampere rating of the receptacle?
N new_ee Senior Member Sep 29, 2005 #3 Re: 120V Duplex Receptacles on 30A Breaker? Well can you get a standard double duplex in more than 20A rating? Also could someone point me to the code sections I should be looking at? Somewhere around 210 maybe?
charlie b Moderator Staff member Location Lockport, IL Occupation Retired Electrical Engineer Sep 29, 2005 #4 Re: 120V Duplex Receptacles on 30A Breaker? Table 210.21(B)(3).
N new_ee Senior Member Sep 29, 2005 #5 Re: 120V Duplex Receptacles on 30A Breaker? Thanks I had a request to get double duplex receptacles on a 30A branch circuit. From my research it looks like thats not going to happen.
electricman2 Senior Member Location North Carolina Occupation Retired Electrical Contractor Sep 29, 2005 #6 Re: 120V Duplex Receptacles on 30A Breaker? The NEMA configuration for 120V, 30A is 5-30. I have never seen this in a duplex.
steve66 Senior Member Location Illinois Occupation Engineer Sep 29, 2005 #7 Re: 120V Duplex Receptacles on 30A Breaker? If your client wants to plug standard 120V, 15 amp and 20 amp devices into a receptacles on a 30 amp circuit, you are right. That is not allowed by the code. Steve