120V Duplex Receptacles on 30A Breaker?

Status
Not open for further replies.

new_ee

Senior Member
Re: 120V Duplex Receptacles on 30A Breaker?

Well can you get a standard double duplex in more than 20A rating?

Also could someone point me to the code sections I should be looking at? Somewhere around 210 maybe?
 

new_ee

Senior Member
Re: 120V Duplex Receptacles on 30A Breaker?

Thanks :) I had a request to get double duplex receptacles on a 30A branch circuit. From my research it looks like thats not going to happen.
 

electricman2

Senior Member
Location
North Carolina
Occupation
Retired Electrical Contractor
Re: 120V Duplex Receptacles on 30A Breaker?

The NEMA configuration for 120V, 30A is 5-30. I have never seen this in a duplex.
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
Re: 120V Duplex Receptacles on 30A Breaker?

If your client wants to plug standard 120V, 15 amp and 20 amp devices into a receptacles on a 30 amp circuit, you are right. That is not allowed by the code.

Steve
 