iggy2
Senior Member
- Location
- NEw England
We have a project with existing Sq D QO loadcenters each with a 2 pole, 20A CB feeding an electric kick space heater (1500 W = 6.25A). Part of the project is to add a piece of electric baseboard (EBB) in the bathroom. I would like to use 120 volt baseboard, just to keep the voltage in the bathroom, and at the wall mounted, line voltage thermostat lower. Is there any reason one pole of the 20A 2P CB cannot feed the EBB (500W = 4.2A), as well as the existing kick space heater?
I was thinking the 120V load would then be on a multi-wire circuit, which could only feed line-to-neutral loads. But since the 2 loads do not share a neutral, that does not seem to be the case. Also, exception 2 of 210.4 would allow the line-to-line load, since the 2P CB would open all ungrounded conductors simultaneously.
(QO breakers are listed for 2 wires, but that's not really my question.)
Thanks.
I was thinking the 120V load would then be on a multi-wire circuit, which could only feed line-to-neutral loads. But since the 2 loads do not share a neutral, that does not seem to be the case. Also, exception 2 of 210.4 would allow the line-to-line load, since the 2P CB would open all ungrounded conductors simultaneously.