I have an application where I'd like to specify 208V low bay MH lights, but I notice that "bug eyes" only come in 120V or 277V. Do you see anything wrong with placing the 120V bug eyes on one unswitched, ungrounded conductor of the normal 208V lighting, as long as I show a neutral to the bug eyes, as well? It seems that 240.20 would allow this with any tied or multi-pole breaker with internal common trip.
Another option I've thought about would be to run a single 120V circuit (from the same panel) to all the emergency fixtures and have a lock-on device per 700.12(F) exception. There are 4 normal lighting circuits in the same room.
Another option I've thought about would be to run a single 120V circuit (from the same panel) to all the emergency fixtures and have a lock-on device per 700.12(F) exception. There are 4 normal lighting circuits in the same room.