Would it be a violation to use a 2p 277v Rated switch with the 277v for the lighting run through one side of the switch and the 120v run through the other side ?
I say it is,but a friend of mine says that it is'nt.
The lights and the fan need to be controlled off of the same switch.
I've always used a contactor with a 277v coil and ran the 120v circuiit thru the contactor.
I would also have an issue with the 2 different voltages available on the switch, much like a multiwire branch circuit to a receptacle, but there would be no way to tye the handles together to since the power comes from 2 different sources.
He also claims that the 300v between issue does not come into play since the 2 voltages are not "between" but are on the same switch.
I am so used to doing things the right way, that when I get into a disagreement on crazy stuff like this, I dont know how to respond to it.