Hello,
I am an master electrician in NYC.
I have an potential job but conditions of it are concerning me.
So, client is combining 3 apartments on the top, 17th floor of the multifamily residential building.
Each apartment is fed by 120V 60A 2 wire feeder with 3 AWG conductors in steel conduit.
Building is old and they have installed 3 phase 4 wire feeders for 3 apartment on top of each other. Sharing the grounded conductor between those three apartments.
Distance from overcurrent protection to apartment panels is 250’ and as per my calculations voltage drop is exceeding allowable 4% drop as per 2011 NYC code.
Load calculations as per engineer is 60A on each feeder.
I just wanted your opinion if these installation, loading #3 wire on 250’ 3 phase system with 60A is allowed. Does it pose any overload or overheating of conductors?
Thank you very much!
I am an master electrician in NYC.
I have an potential job but conditions of it are concerning me.
So, client is combining 3 apartments on the top, 17th floor of the multifamily residential building.
Each apartment is fed by 120V 60A 2 wire feeder with 3 AWG conductors in steel conduit.
Building is old and they have installed 3 phase 4 wire feeders for 3 apartment on top of each other. Sharing the grounded conductor between those three apartments.
Distance from overcurrent protection to apartment panels is 250’ and as per my calculations voltage drop is exceeding allowable 4% drop as per 2011 NYC code.
Load calculations as per engineer is 60A on each feeder.
I just wanted your opinion if these installation, loading #3 wire on 250’ 3 phase system with 60A is allowed. Does it pose any overload or overheating of conductors?
Thank you very much!