- Location
- Tennessee NEC:2017
- Occupation
- Semi-Retired Electrician
Am I correct in thinking you can't run a piece of 120V equipment off a 240V GFCI without tripping the GFCI?
I have a timer for a pool pump that is 240V. It is fed from a 240V GFCI. They have a UV light for cleaning the pool that can only be on when the pump is running. Normally I do this with the timer but the cleaning equipment is usually also 240V.
I'm thinking if I tried to take 120V off one of the load sides of the timer the GFCI will see that as a fault or imbalance since I would also have a neutral. The current on the 120V would return on the neutral and not the other leg of the 240V therefore cause the GFCI to sense an imbalance.
Is this correct or is my brain "fuzzy" again?
I have a timer for a pool pump that is 240V. It is fed from a 240V GFCI. They have a UV light for cleaning the pool that can only be on when the pump is running. Normally I do this with the timer but the cleaning equipment is usually also 240V.
I'm thinking if I tried to take 120V off one of the load sides of the timer the GFCI will see that as a fault or imbalance since I would also have a neutral. The current on the 120V would return on the neutral and not the other leg of the 240V therefore cause the GFCI to sense an imbalance.
Is this correct or is my brain "fuzzy" again?