I am only reading 60v coming out of a new halogen flood...is this right? Lights work fine, but shouldnt it be 120v?
 
When I remove the bulb and put a meter to the contacts it reads roughly 60 volts on each flood. I thought I should read 120 volts.
 
Pardon me if I don't see the obvious. What does the voltage read at the outlet? If it's the same you have a missing nuetral.
 
Is this a quartz Halogen fixture, and are you using a digital meter. Some of the quartz floods have lamp contacts that disconnect from the source when you take the lamp out. You might be getting phantom voltage.
 