120V max in dwelling occupancies

Status
Not open for further replies.

mguzik

New member
Is the use of 277V lighting fixtures in a dwelling occupancy a violation of NEC 210.6 (A) and would it be allowed by any other code section like NEC 410?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
The way I read it is that you cannot use 277v for lighting in a dwelling based on 210.6 (A). Article 210.6(C) alows 277v but I take that to mean in non residential if it met the following choices listed.
 

norcal

Senior Member
Where do you get 277v in a dwelling?



When you have a bootleg MIL unit attached to a shop w/ a 480Y/277V service, I kid you not........


The electrical is a sight to see

DSC03080.jpg


DSC03079.jpg


DSC03078.jpg


480V submersable pump, see anything wrong? With the other 2 it's easier to ask if anything is right.
 
Last edited:

480sparky

Senior Member
Location
Iowegia
If these are condos then I believe the 277 may be used outside the building for the exterior lights.

Seems it would be a poor design to install a 277/480v service for a handful of wall packs, then have a humongous 480-120/208 transformer to run 99.99% of the load.
 