So a friend of mine lives in a RV park. He has a 30a 120v service and is getting 450$ power bills.
So by my math if they’re maxing out their 30 amps at 80%
its 24x120=2.8kw 2.8x24 hours x30 days is 2016kwh and at 18 cents a kWh the RV park charges
2016x0.18 equals 362.88$
So unless my math is bad 450$ is impossible without blowing a breaker.
We turned everything on and it was only 15a
The meter base is analog, it’s a 120v meter but the neutral is on one leg and the hot on the other.
There is no screw on the back of the meter to isolate the neutral, but I assume it being 120v meter it’s not actually reading the neutral.
many ideas?