First see whether you have the needed ground detector. If it is required, adding your transformer will not change that.I was curious if there was a way to set a transformer and add a 120V single phase sub panel off an old 1950's 240V Delta Ungrounded Service ? If so, how would you go about this ?
First see whether you have the needed ground detector. If it is required, adding your transformer will not change that.
Second, you can add a transformer with a 220V primary and either a 120V secondary or a 240V center tapped secondary.
In either case it will be wired as an SDS.
You will ground one conductor of the secondary.
The placement and size of primary and secondary OCPD is something I will leave for later.
While not disagreeing with the notion that a three phase panel can be more useful than a single phase, in this case the OP stated the existing service is 240V Delta.I suppose a single phase sub panel will keep the cost down; but I would consider the versatility of a 3 phase panel. You mentioned VFD's, which suggests more 3 phase capability could be useful. A 120/208 volt panel can provide for future 3 phase loads as well as convenience outlet circuits. A 3 phase Delta/Wye transformer feeding a 3 phase panel may make sense.
I have a feeling there's more to the whole picture than we are being led to believe. I can't imagine a premises having only a 240V 3? 3W ungrounded system with no means for 120V circuits. Sounds more like a economics approach than purely electrical.
208/120V 3? 4W or 240/120V 3? 4W would likely require POCO to run a neutral and EC to continue through service equipment.Is the 204V delta service currently under heavy use?
Could you have the power company reconnect their transformers to provide a 120/240 single phase or a 208/120 three phase service?