120v Sump pump with 5 wires?

ramsy

NoFixNoPay Electric
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
Anyone seen this connector before?
5 wires to a 120v convenience outlet.

1st image shows factory T-connector cord cap, for 2 cords, only 1 with EGC.
Megger passes from each of 4 wires to EGC, but not between each other.

2nd image shows it hard wired, whites to GFCI load Neutral, blacks to GFCI load hot.

Flip switch blows breaker 100ft away, before GFCI can trip.
 