120v to 240v - Dumb question

Status
Not open for further replies.

mark32

Senior Member
Location
Currently in NJ
I'm almost too embarrassed to ask but can one derive 240v from 120v? I spoke to someone today that claims an electrician friend told him he could do so, reason being, guy bought a 240v dryer but he only has 120v coming into his apt.
 
Funny you should ask. Read the "Is this a real neutral?" thread. The answer to both your question and that thread title is yes.

For a clothes dryer, the autotransformer would need to be rather hefty.
 
and so would the cir feeding it.

30amps for the dryer, you would need 60a of 120 for the transformer (round numbers with no calculating)


Indeed, presuming of course that we are talking about an electricly heated dryer, as most are.
Gas heated dryers exist that require electricity only for the tumble action and controls, these have a much smaller power draw.
If produced for the USA market I would expect a gas dryer to be 120 volt, but of course it may be intended for a 230/240 volt country.
 
I'm almost too embarrassed to ask but can one derive 240v from 120v? I spoke to someone today that claims an electrician friend told him he could do so, reason being, guy bought a 240v dryer but he only has 120v coming into his apt.

What size is his main breaker? I dont think this is going to happen for him.
 
Thank you guys for the kind responses. Word of this install didn't come to me directly from the customer but through a co-worker so I didn't get much info. After some thought, and now I see others thinking the same, is a concern, or wonder rather, what size the service is in this situation. If he only has 120v coming in, in all likelihood it couldn't be that big, what, 60a tops? I'm not too worried though about this guy's predicament though, he's not a customer of mine, but the fact that I didn't/don't know much about auto transformers, which led me to the title of this thread. After eight years in the trade (Residential, commercial, industrial) I've never had to use one, thus my limited knowledge on this item. Sometimes I do feel dumb when I can't answer someone confidently or screw up in other ways. For example, last week I worked with a buddy of mine and he asked me to change out an in wall timer with another and to change the cfl's to regular incandescents, because the new timer wasn't rated for them. After hooking up the timer, live, he comes over, "Blah, that timer's not rated for cfl's" I said I know, "But the cfl's are on right now, that damages the timer". You see, I didn't know that the timer automatically comes on, my bad.
 
Another issue is that I believe by code, if he has a 240V outlet in a laundry area, it must have a dryer vent and vice versa. So conversely if he only has 120V in the apartment, he will NOT likely have a dryer vent, and using a dryer indoors without venting is a really really bad idea! He may end up having to pay for major moisture damage to the apartment building!
 