electro1 said:
...can you explain please. thanks.
I don't know. I'll make a stab at it
electro1 said:
I'am trying to get the minimum load. ...
The load is what it is. No matter how you arrange it, it's still 3 - 400W lamps.
electro1 said:
...if I have 3 400watt lamps pulling 11amps and I change the taps to feed 208 V which uses 6.8 amps per phase. ...
You left some information out, so I'm going to have to guess:
1. The 11A was with all three lamps connected to one 1phase 120V circuit (two wires, hot and neutral)
2. The lamps have multi-tap ballasts, likely 120V, 208V, 240V, 277V
3. With all three lamps connected to one 1phase 208V circuit (two hot wires), they draw 6.3A.
If any of this is wrong, then throw the rest out.
electro1 said:
...Do I add the two phases together making it 13.6 amps total or is it just 6.8amps total? ....
No. Current always forms a loop. What goes out, has to come back. The Mathematical way to say this is, "For any point, (Summation I) = 0 Or, the current entering the lamps equals the current leaving the lamps. So, The 6.8A entering one end of the lamps is the same current leaving the other end of the lamps.
If you want the apparent power delivered to the lamps, then one takes the current through the lamps (6.8A or 11A) times the voltage across the lamps (208V or 120V)
120V X 11A = 1320VA
208V X 6.8A = 1310VA
I would call that the same load.
carl