No. UL test breakers for every possible loading configuration, 2-pole breakers are tested for 1-pole loads.Are there any Nec requirements or safety concerns to support not using a two pole breaker on a 120vac grounded neutral system?
The NEC requires switched neutral breakers for gas station pumps.I have never seen the grounded leg of a 120vac circuit protected by a circuit breaker before now.
Use a common-trip breaker. If the customer wants to waste money, that's their problem.I have never seen the grounded leg of a 120vac circuit protected by a circuit breaker before now. I am not sold on the idea of a 2 pole breaker on a 120vac, but am struggling to come up with an argument for the client that is requesting the 2 pole breaker.
If a fault occured and the 120vac neutral leg opened could you possible have a charged leg awaiting a source to ground. What problems could occur if the neutral leg opened on a fault or overload?
I have never seen the grounded leg of a 120vac circuit protected by a circuit breaker before now. I am not sold on the idea of a 2 pole breaker on a 120vac, but am struggling to come up with an argument for the client that is requesting the 2 pole breaker.
If a fault occured and the 120vac neutral leg opened could you possible have a charged leg awaiting a source to ground. What problems could occur if the neutral leg opened on a fault or overload?