125 amp Service Grounding

Status
Not open for further replies.

joeyjjsdad

New User
Location
TN
My question is based on the 2008 electrical code. I have a question about grounding a service for a outbuilding. It will have no water supply to this building. The 125 amp service will be back to back. Should I run a ground from the meter base into the 125amp main service panel?
And at what spot (meter base or Main Panel)should I bring the #6 ground wire to the ground rod. Thank you
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
From the meter to the interior panel: Phase conductors + grounded (neutral) conductor
The grounding electrode conductor can connect to the neutral buss at the meter or in the panel as far as the NEC is concerned. The power co. may have a preference.
 

kwired

Electron manager
Location
NE Nebraska
Is this service or feeder supplied?

(does it come from the utility or from load side of service disconnect at another building?)

Is it new or existing? There are some things that can differ depending on answer to that.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Is this service or feeder supplied?

(does it come from the utility or from load side of service disconnect at another building?)

Is it new or existing? There are some things that can differ depending on answer to that.

good question... from his term "meter base ", I assumed service.
 