125 Amp Sub Panel Wire Size

Status
Not open for further replies.

millwoodva

New User
Location
Millwood, VA
Subpanel install in a pole building. House is wired for 400 amp service..
180' total... (80' from main panel to house wall exit.. underground feed 100' to pole bdg)
planning on aluminim conductors... Thinking continuous run of 2/0-2/0-2/0-1.
Though if 3 ea. 1/0 will carry the load that distance.. prefer that less expensive route..
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
What is the load on the building? You cannot do a voltage drop calc without knowing the amperage. If you go for the 125 amp load than 2/0 would be correct

BTW, welcome to the forum
 
Last edited:

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
#1/0 will work for 90 amps, as Dennis pointed out in the worst case scenario #2/0 would work.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
If the 125A subpanel were fed from a 90A breaker at the main panel, and the calculated load was <90A, then #2 Al could be used, yes?

Sure but there is nothing in the OP that suggests that they want to use less than a 125 amp OCPD. The minimum permitted conductor would be #1/0 Al with a 125 OCPD. At 90 amps of load your voltage drop would still be under the 3% recommended threshold. As Dennis stated if you wanted the full 125 amps then with the 3% maximum recommended VD you would need to go up to #2/0.
 