I am ready to learn why this is reasonable and not weird. I agree, it's legal to code, but it doesn't make a whole lot of sense.Originally posted by iwire:
...use 240.4(B) move up to next standard size OCP...
George IMO you have a perfect handle on it.Originally posted by georgestolz:
I am ready to learn why this is reasonable and not weird. I agree, it's legal to code, but it doesn't make a whole lot of sense.
All you seem to be missing is 240.4(B)Originally posted by james wuebker:
Sorry guys but I believe he should be using #1 copper proving all lugs are rated 75c. Yes # 2 copper will get you 115 amps. Yes the load might not get that high but you never know. You wouldn't put # 2 copper in a 200 amp panel even if the load was going to be low. Maybe I'm missing something in this thread. Let me know if I am.
Thanks!
Jim
If you personally do not want to use this allowance thats fine, but it is code compliant.240.4(B) Devices Rated 800 Amperes or Less. The next higher standard overcurrent device rating (above the ampacity of the conductors being protected) shall be permitted to be used, provided all of the following conditions are met:
(1)The conductors being protected are not part of a multioutlet branch circuit supplying receptacles for cord-and-plug-connected portable loads.
(2)The ampacity of the conductors does not correspond with the standard ampere rating of a fuse or a circuit breaker without overload trip adjustments above its rating (but that shall be permitted to have other trip or rating adjustments).
(3)The next higher standard rating selected does not exceed 800 amperes.
Actually, 310.15(B)(6) covers services and feeders, so running 2/0 Cu to 200A subpanel would be fine.Originally posted by james wuebker:
iwire
That's a new area for me. So it's telling me that it's OK to run 2/0 copper for a 200 amp sub panel. To me I would be running 3/0. Now if it's a service then we can use 310.15(B). 240.4(B) it's new meaning to me. Yes, 500 mcm I've seen it run for a 400 amp service. We'll thanks for the insight.
Jim
True for some installations but that table applies only to dwelling units that are fed from a 240/120 system.Originally posted by jeff43222:
Actually, 310.15(B)(6) covers services and feeders, so running 2/0 Cu to 200A subpanel would be fine.
I want to clarify something. For any service other than residential, single phase 120/240 Delta:so running 2/0 Cu to 200A subpanel would be fine.
I agree with JW. This is the key question, and it is a question that "kg18" has not yet addressed. You have to start with a load calculation, per 220. Then you size the conductors on the basis of the results of that calculation.Originally posted by jwelectric:
In other words the calculated load for the sub panel would need to be 115 amps or less.
I wouldn't call a residential 120/240 volt system a Delta system. Delta implies that it's a portion of a three phase system. It's simply a center tapped, 3 wire, single phase system.For residential, 120/240 Delta only, see 310.15(b)(6) which will let you protect 2/0 with a 200 Amp OCPD.
Actually Charlie I believe as an electrician working under the NEC I can do just that.Originally posted by charlie b:
We can't leave the customer with, "well, if you add load and go beyond 115 amps, we'll get out the marshmellows."
Whoever adds load better check what has been installed.230.90(A)Exception No. 3: Two to six circuit breakers or sets of fuses shall be permitted as the overcurrent device to provide the overload protection. The sum of the ratings of the circuit breakers or fuses shall be permitted to exceed the ampacity of the service conductors, provided the calculated load does not exceed the ampacity of the service conductors
I agree with this statement, and my earlier statement does not contradict it. What I said is that when the panel is first installed, if we do not know the load (i.e., no load calc), then a 125 amp panel needs a 125 amp feeder (or service) and an overcurrent device (or devices) that will protect the 125 amp conductors.Originally posted by iwire: It will be the responsibility of the electrician adding load to the panel to ensure it has the capacity.
How did I choose a 125 amp panel without having an idea what the load was going to be?Originally posted by charlie b:
What I said is that when the panel is first installed, if we do not know the load (i.e., no load calc), then a 125 amp panel needs a 125 amp feeder (or service) and an overcurrent device (or devices) that will protect the 125 amp conductors.