AWinston
Member
- Location
- Murrieta, Ca
So I am sizing the service for a growing facility (a lot of lights and AC units). I know NEC 210.19 states that the minimum ampacity of a conductor for continuous loads shall be 125%. When sizing the panelboard, am I supposed to size the panel according to that as well? The total connected load is 1512A, but the Total estimated demand after applying the 125% demand rule to certain loads is 2223A. Is my panelboard/switchboard supposed to be sized for 2223A? I'm second guessing myself because one of the "engineers" at the power company is saying otherwise.